My POH does not go into detail on this-

Could someone define the difference between the two alternator circuit breakers for me. I hate to just assume....

Thanks,

Rob

IMG_9108.jpg

Posted

The ALT breaker is on the output of the alternator. The ALT FLD breaker is for the voltage regulator.

If you pull the ALT FLD breaker, you will turn off the voltage regulator which removes excitation from the alternator so it will not make any power. It is mostly there to protect the regulator. Sometimes if the alternator stops working, power cycling the regulator will reset it and it will start working again.

  • Like 2
Posted

Circuit breakers exist to protect wiring. They have a secondary use for deactivating a circuit manually if they are the push on, pull off type. 

Some voltage regulators react to an overvoltage failure by intentionally causing a short in the field circuit to trip the field breaker and disable the alternator.

The 70 amp breaker protects the wire between the alternator and the main bus. The alternator cannot supply enough current to trip this breaker but the battery could if there were a short circuit in this wire.

  • Like 2

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.